Hard start kit plus a soft starter on same compressor motor somewhat conflict with one another I would think.
First thing is making sure you are not starting with residual pressure in the system from the last run. Delay timers made for this are pretty inexpensive, maybe only $10 -15 at HVAC supply house. If you still need hard start kit when there is no residual pressure, you probably have a compressor that isn't going to last much longer. Low volts, undersized circuits, small transformer - all add some the characteristics of a soft starter, but if low volts is on the service/feeder and not just the branch circuit other items will see the effects as well and will be easily noticed with lighting particularly LED lighting.
First thing is making sure you are not starting with residual pressure in the system from the last run. Delay timers made for this are pretty inexpensive, maybe only $10 -15 at HVAC supply house. If you still need hard start kit when there is no residual pressure, you probably have a compressor that isn't going to last much longer. Low volts, undersized circuits, small transformer - all add some the characteristics of a soft starter, but if low volts is on the service/feeder and not just the branch circuit other items will see the effects as well and will be easily noticed with lighting particularly LED lighting.