jaggedben
- Northern California
- Solar and Energy Storage Installer
So I'm installing a system with two high voltage LG batteries and it appears I need to use a fused combiner to parallel them. Max voltage for each battery unit is 570V. 'Peak current' is 18.9A but no short circuit current rating is listed. The circuit is ungrounded. A battery combiner is a first for me, and I have some questions:
Under the 2014 NEC...
- For two batteries, would a battery combiner be required by the Code if not required by the manufacturer, if all wiring were sized to handle current from both batteries?
- Under the 2014 NEC, would you say both positive and negative need to be fused, or just one side (i.e. positive)?
- Does the code require such a combiner to be listed?
Opinions wanted. There doesn't seem to be much code guidance on this in the 2014, or even the 2017.