Existing transformer size in a telephone exchange is 500 KVA. The breaking capacity of the secondary side breaker fed by bus bar from the transformer is 55kA. The transformer suffered internal fault and has to be replaced. The spare transformer available at another distant exchange is 750KVA, 415V, 4% impedance. The question is if the existing breaker need to be replaced for the 750 KVA replacement transformer. Thanks.