On higher temp cables for example #14 Type Z rated at 150c the value in 310.15(B)18 is 34amps. In what condition can I use it at full ampacity?
In 110.14(C)(1) it speaks of the terminations limiting the cable use?
So I imagine there is no 150c Connectors?
So other than for ambient temp correction what use is this cable?
To me from 110.14(C)(1)(a) I will not be able to use the Type at over 15amps
In 110.14(C)(1) it speaks of the terminations limiting the cable use?
So I imagine there is no 150c Connectors?
So other than for ambient temp correction what use is this cable?
To me from 110.14(C)(1)(a) I will not be able to use the Type at over 15amps