dm9289
Industrial Maintenance Electrician
- Location
 - Pennsylvania
 
- Occupation
 - Industrial process repair/ maintenance Electrician
 
On higher temp cables for example #14 Type Z rated at 150c the value in 310.15(B)18 is 34amps. In what condition can I use it at full ampacity? 
In 110.14(C)(1) it speaks of the terminations limiting the cable use?
So I imagine there is no 150c Connectors?
So other than for ambient temp correction what use is this cable?
To me from 110.14(C)(1)(a) I will not be able to use the Type at over 15amps
	
		
			
		
		
	
				
			In 110.14(C)(1) it speaks of the terminations limiting the cable use?
So I imagine there is no 150c Connectors?
So other than for ambient temp correction what use is this cable?
To me from 110.14(C)(1)(a) I will not be able to use the Type at over 15amps
				