I'm guessing water got in thru the broken/missing cover, corroded the internals, and created a short between hot and neutral, resulting in what is pictured; receptacle burning from the inside out. I've seen numerous 250V 20A simplex receptacles do the same in PTAC sub-bases when the sleeve is damaged, allowing condensate to run all over the receptacle.

What is the imprint on the receptacle face in the upper left part of the pic? Doesnt appear to be an older WR designation.
Smart lock designatinon AFAICT.

It may be old enough installation that WR wasn't required yet.

Even with a good cover a weep hole in bottom of box would still drain any water that does end up inside.
 
I haven't seen it bunches but I seen it more than once.
I have seen it even more often when there was a raceway entering the top of the box and no weep hole to drain out condensation. Seldom if ever seen it with NM cable fed in the back of the box like pictured in op.
 