The only time I have heard the term "Hogan grounding" is for grounding multiple transformers that are on multiple floors to a common grounding electrode.
For example, if one had a ten story building and wanted to use the concrete encased electrode for the transformers, they could run a piece of 3/0AWG from the top floor to the bottom floor and install grounding electrode conductor taps from each transformer to the common grounding electrode conductor. The tap conductors would be sized in accordance with Table 250.66, based on the size of the ungrounded secondary conductors of the individual transformer it serves.