Hogan Grounding

Status
Not open for further replies.

pmariu

New member
When you have to use hogan groundig ,and how you doing it, can somebody
explain it please Thank you
 
The only thing I know as a "Hogan" is the big busbar (generally 2" x 1/4") that they run up the utility chase of tall buildings for everyone to bond everything that needs bonded to that bar along the way. That bar is connected to the building steel, water lines, and any other grounding electrodes already.
 
The only time I have heard the term "Hogan grounding" is for grounding multiple transformers that are on multiple floors to a common grounding electrode.
For example, if one had a ten story building and wanted to use the concrete encased electrode for the transformers, they could run a piece of 3/0AWG from the top floor to the bottom floor and install grounding electrode conductor taps from each transformer to the common grounding electrode conductor. The tap conductors would be sized in accordance with Table 250.66, based on the size of the ungrounded secondary conductors of the individual transformer it serves.
 
My understanding is the term "Hogan" came from an inspector named Hogan in the Chicago area that required (or perhaps permitted) this type of system for multiple transformers.
 
That's how it was explained to me in code class last time around. There was another term but I can't remember it right now. Only for xformers though.
 
Whew! for a minute there I was afraid I was going to be the only one asking what the heck that was.

I didn't know the term, but at least I knew what it was after it was explained.
 
brian john said:
Colonel Klink anyone?

Here ya go...

klink.jpg



Hogannnnnnnnnnnnnn!!!!
 
In my biz we call it a Vertical Riser which can be a buss bar or large copper cable rising vertically through a building shaft, and bonded to building steel as it rises the length of the building. It is a great ground reference when used correctly.
 
Hogan is from chicago

Hogan is from chicago

The term "Hogan ground" is named for a former president of local 134 (chicago IBEW). The Hogan grounding system is a continuation of the groundind electrode conductor. It is typically used in high rise builings and required by Chicago code.
 
dereckbc said:
In my biz we call it a Vertical Riser which can be a buss bar or large copper cable rising vertically through a building shaft, and bonded to building steel as it rises the length of the building. It is a great ground reference when used correctly.

Can you elaborate on the used correctly part? How do people screw it up, other than extra neutral/ground bonds?
 
Bill Hogan was the chief electrical inspector in Chicago through the 1960's into the 70's. He was tough and was the quinessential AHJ. "Rumors" of inspector pay-offs in the late 70's forced the City to completly re-structure the Builidng Department.

He did in fact "require" this form of transformer grounding which bares his name.

He was a Chicago classic.

You could look it up
 
jdsmith said:
Can you elaborate on the used correctly part? How do people screw it up, other than extra neutral/ground bonds?
By not bonding it to building steel at every floor or every other floor as it rises
 