Comments back from DERM and FIRE department.
This is going to be real fun!!
A.5. THE SIZE OF THE FUEL TANK SHALL BE SHOWN CONSISTENTLY THROUGHOUT THE WINGS 650-G OR 966-G? CALL ON PLANS THE SIZE OF THE PROPOSED FUEL TANK. N PICAL DETAILS OR TABLES WILL BE ACCEPTED. PROVIDE DETAILS ON PLANS AND M Y ACCORDINGLY. CALL ON PLANS ALL EQUIPMENT BEING INSTALLED. NO TYPICAL DETAILS WITH OPTI UMBERS WILL BE ACCEPTED UNLESS THE OPTIONS TO BE INSTALLED ARE CLEARLY CA OUT ON PLANS. A TYPICAL DETAIL WITH AN OPTION NUMBER DOES NOT MEAN THAT RTICULAR PIECE OF EQUIPMENT IS PROPOSED. PROVIDE DETAILS ON PLANS AND MOD ACCORDINGLY. ONLY EQUIPMENT BEING PROPOSED SHALL BE SHOWN ON PERMIT SET OF PLANS. NO T
AL DETAILS WITH ALL POSSIBLE OPTIONS ARE ACCEPTED. PROVIDE DETAILS ON PLA ND MODIFY ACCORDINGLY. A FILL PORT WITH AN OVERFILL SENSOR IN THE FILL PORT IS CALLED OUT ON PAG WHAT DOES THAT MEAN? THE FILL PORT IS JUST THE ACCESS TO THE TANK AND TH LL DROP TUBE, THERE IS NO ROOM FOR A LEVEL SENSOR. MODIFY PLANS ACCORDING A.6. ALL EQUIPMENT TO BE INSTALLED MUST BE APPROVED BY THE FLORIDA DEPART OF ENVIRONMENTAL PROTECTION (FDEP) SO PROVIDE A STATEMENT ON PLANS THAT OF THE APPLICABLE EQUIPMENT WILL BE FDEP APPROVED. C.2. INDICATE ON PLANS WHETHER THE PROPOSED FUEL DIESEL TANK TO BE INSTAL WILL BE NEW, RELOCATED OR PROPERLY RECERTIFIED. MODIFY PLANS ACCORDINGLY.
C.7. CLARIFY AND CALL ON THE DRAWINGS IF ANY HIGH FUEL LEVEL SENSOR IS BE PROPOSED, ALSO SHOW ON PLANS THE LOCATION OF THE HIGH LEVEL SENSOR. PROVI ETAILS ON PLANS AND MODIFY ACCORDINGLY. THE FUEL TANK SHALL BE EQUIPPED WITH AN OVERSPILL CONTAINMENT BOX AT THE PORT. SHOW ON PLANS THE LOCATION AND CALL THE OVERSPILL PREVENTION BOX. IDE DETAILS AND MODIFY ACCORDINGLY. SHOW ON PLANS THE LOCATION OF THE OVERFILL PREVENTION ANNUNCIATOR PANEL O NSOLE, CALL THE CONNECTION OF THE HIGH FUEL LEVEL SENSOR TO THE PANEL AND TYPE OF ALARM I.E. VISUAL, AUDIBLE, ETC. NOTE THAT THE OVERFILL ANNUCIAT HALL BE AS CLOSE AS POSSIBLE TO THE FILL PORT. PROVIDE DETAILS AND MODIFY
NS ACCORDINGLY. C.8. SHOW ON PLANS THE LOCATION AND CALL THE INSTALLATION OF THE TANK INT ITIAL LEAK SENOR. PROVIDE DETAILS ON PLANS AND MODIFY ACCORDINGLY. SHOW ON PLANS THE LOCATION OF THE TANK INTERSTITIAL ANNUNCIATOR PANEL OR OLE, CALL THE CONNECTION OF THE TANK INTERSTITIAL LEAK SENOR TO THE PANEL THE TYPE OF ALARM I.E. VISUAL, AUDIBLE, ETC. PROVIDE DETAILS AND MODIFY S ACCORDINGLY. C.9. SHOW ON PLANS HOW THE FUEL TANK IS BEING ANCHORED TOP THE CONCRETE S I.E. BOLTS, STRAP, ETC. PROVIDE DETAILS ON PLANS AND MODIFY ACCORDINGLY. G.3. COMPLETE AND SUBMIT THE ENCLOSED SPILL PREVENTION AND RESPONSE PLAN
P) FORM. NOTE THAT THE ENCLOSED FORM REQUIRES TO BE NOTARIZED AND A LIST HE EMERGENCY EQUIPMENT TO BE USED FOR SPILLS MUST BE PROVIDED. A LIST OF MATERIALS/EQUIPMENT TO HANDLE MINOR SPILLS (I.E. CAT LITTER, SA ABSORBENT MATS, SHOVEL, ETC.) SHALL BE ALONG WITH THE SPRP. MORE COMMENTS MAY FOLLOW PENDING INFORMATION SUBMITTED. NO HAND WRITTEN N AND/OR CORRECTIONS WILL BE ACCEPTED. SHOULD YOU HAVE ANY QUESTION CONCERNING THIS MATTER, PLEASE FEEL FREE TO ACT ME AT
. APPLICATION IS FOR INSTALLATION OF A 275KW GENSET, WITH A DOUBLE-WALL, 1,000 GAL, ABOVE GROUND, SUB-BASE DIESEL TANK. SUBMITTED DOCUMENTS INCLUD BOUNDARY SURVEY, ELECTRICAL SITE PLAN AND DETAILS (DWP1), A SITE PLAN (DW LOCATING THE GENSET, AND DWG3, WHICH SHOWS "TRAMONT" ISOMETRIC UNIT DETAI TANK WEIGHTS AND DIMENSIONS, AND A SITE AERIAL PHOTO. ADDITIONALLY, A PAC OF 8 ? X 11 SHEETS, LABELED "TRAMONT; SUBMITTAL MANUAL", PROVIDES SYSTEM COMPONENT INFORMATION AND DETAILS. HOWEVER, THE PACKAGE DOES NOT INCLUDE CERTAIN INFORMATION REQUIRED FOR REVIEW, AS SET FORTH IN THE CIRCULAR LAB
"MIAMI DADE COUNTY CHECKLIST FOR PERMANENT INSTALLATION OF GENERATORS", W INCLUDES THE FOLLOWING LISTED INFORMATION: 2. PLANS PROVIDED WITH DETAILS TO INDICATE COMPLIANCE WITH NFPA 110 (2002 ED). 3. IDENTIFY CLASS, TYPE, AND LEVEL OF THE GENERATOR IN ACCORDANCE WITH NF 110, CHAPTER 4. 4. CLEARLY IDENTIFY THE LOCATION OF THE REMOTE ANUNCIATOR. 5. CLEARLY IDENTIFY THE LOCATION OF THE EMERGENCY SHUT-OFF CONTROLS REQUI BY NFPA 110 (5.6.5.6). NOTE THAT MDFR IS LOOKING FOR A DISTANCE SEPARATIO 20 FT BETWEEN THE GENSET AND SWITCH.
6. IDENTIFY LOCATION OF THE FUEL CONTAINERS AND GENERATOR WHEN LOCATED IN AREAS SUBJECT TO VEHICULAR TRAFFIC. 7. PLANS MUST BE PROVIDED WITH DETAILS TO INDICATE COMPLIANCE OF THE FUEL SYSTEM, AND/OR FUEL STORAGE SYSTEM TO BE USED (NFPA 30 (2000 ED); NFPA 37 (1998 ED); NFPA54 (2002 ED); NFPA 58 (2002 ED). 8. FINALLY, ALSO PLEASE INDICATE SIGNAGE REQUIRED BY THE LISTED STANDARDS AND/OR NFPA 704. 9. UPON RECEIPT OF THE INFORMATION ABOVE, THE REVIEW CAN BE COMPLETED.