9-10 KW 240v ranges in a home economics classroom, fed from a 120/ 208v feeder.
What is the calculated load for the ranges on this feeder? Looking for amps?
The answer provided is 88 Amps. Referencing Table 220.56.
I took the total of all 9 ranges kw at 10 kw, added them together and got 90000.
Then factored in the derating per Table 220.56 = 90000 VA X .65 = 58500 VA
Then I take 58,600 VA. and reduce to amperage by Dividing 58500/208 X1.732 (360)= 162.5 Amps
What am I missing ... As always, any assist would be appreciated.