HOME ELECTRICAL GENERATORS - Gas Meters and Regulators

Status
Not open for further replies.

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Gas meters and regulators are typically sized for a specific cubic feet per minute flow at the time of installation, based on the amount of British Thermal Units (BTUs) required by the appliances in the dwelling. When our pool was being built, the contractor determined that our current gas meter was too small for the pool heater. So, he had it increased in size to handle the load.

Is this required in the code ?
 
Line size and pressure are critical in generator applications, lots of " mechanical contractors" do not understand this. Just because the genset will start and run unloaded does not mean all is well, I have seen gensets fall on their face at 50% load because of low pressure/ insufficient BTU input.
 
On HVAC service calls, I also ran into what is called "Flame Rollout". This is usually caused by low gas pressure; the burners have a delayed ignition. Which results in a loud bang.
 