Notice the absence of the word "sub-panel" in the NEC.
A panel was considered an extension of the service. All panels were considered service panels. The premises wiring started at the loadcenters. The neutral was the conductor for fault purposes, it was not considered grounding after the main switch. Grounding is an earth connection, according to the definition in Article 100.
The change of the definition of a "service conductor" in 1996, caused the change to 4/wire feeders. Prior to 1996, the service conductor ended at the loadcenters or all panels. In 1996 the service conductor ends at the first switch.
SE cable with a bare neutral/ground was permitted the same as to the first panel.
Some one decided the bond, at the panel, was re-grounding the neutral. This was when the definition of service conductor changed.