The report stated that GFCI receptacles must be installed in bathroom and kitchen areas. I was wondering if this is true, I stress the word MUST in the statement. I believe, but have no education on the matter, that while it may be a good idea to upgrade, since this was not code when the home was built and no electrical work was done to any circuit that the wording is a mistake. And I do not have any legal cause to install GFCI's. Any thoughts?
If the wiring is untouched since inception, I believe you are correct and the HI is in error. The only way he might be correct is if the bathrooms originally had receptacles in the light fixtures, said fixtures have been replaced with receptacle-less ones (thus leaving no receptacles at all), and 1926 building/NEC required bathroom receptacles... which seems to have come about in 1975.
However, I did find this:
"In jurisdictions that have included the PROPERTY MAINTENANCE CODE as part of their code adoption,
there is a retroactive requirement for at least one receptacle in a bathroom."
poster was from NY, as you are, and it was an HI forum. Here's the link, post #16:
https://www.google.com/url?sa=t&rct...aklgv_wck4Mg3YB6g&sig2=BFn5qEXToqhtauf5tbiEqQ
eta: found this under the PMC:
102.8 Requirements not covered by code. No
structure, the construction and use of which complied
with all code and other such requirements in effect at
the time of construction, shall be required to be
altered in use or structure by the provisions of this
code, except in the case of a clear public safety
hazard.
In the case of a clear public safety hazard,
the code official shall be authorized to enforce a
provision of this code, or other recognized relative
codes, retroactively
http://www.statecollegepa.us/documentcenter/view/7152