Home inspector asking for rec. pigtails
patricknola
Electrical contractor/Generac Dealer
new orleans, La, United States
Electrical contractor.
Good morning, I've got a potential customer who is selling a house. The home inspector returned a report saying the branch circuits are aluminum wire. That all the receptacles need to be updated(which has been done) and that the receptacles need to be pigtailed. Is anyone familiar with what this could possibly mean?
Just a HI's wish. Even with al wiring there is no requirement for pigtails
Two circumstances where wires have to be pigtailed, if you have a multiwire branch circuit that terminates in or passes through the box, the neutrals need to be pigtailed, grounds needs to be pigtailed, in both cases removing the device isn't allowed to interrupt continuity.
I should have mentioned that in my post but it seems as though the OP was saying the HI wanted all receptacles pigtailed.
What article and section did he reference? As Larry stated, HI's do not have real authority, they are simply observers. This doesn't mean I don't have respect for the service they are providing but many times they are a little off base.
Are modern receptacles cu-alr rated? I thought none were anymore, so you need a copper pigtail to the receptacle. Change a receptacle and then AFCI requirements kick in on that circuit.
110.14 requires receptacles and switches be listed for use with Al wire. Likely the "cheapest" work around is the pigtail option.
The other thing that will come up is the home inspector not actually seeing Al wire but tinned Copper, it is a common visual mistake. I would first confirm that what you have is indeed Aluminum.
He said "old Al alloy" not what we use today.
there was nothing really wrong with the "old" alloy. That is mostly an old wives tale. small gauge aluminum wiring got an undeserved bad rap because it was incompatible with the terminations in use at the time. even if you used more modern aluminum alloys it would still be incompatible with those terminations.