roger Moderator Staff member Location Fl Occupation Retired Electrician Jun 16, 2017 #21 Carultch said: yet you have to have a couple/few inches above grade to attach the wire? Click to expand... That's the whole point of this thread, the connection does not have to be above grade or accessible. Roger
Carultch said: yet you have to have a couple/few inches above grade to attach the wire? Click to expand... That's the whole point of this thread, the connection does not have to be above grade or accessible. Roger
FionaZuppa Senior Member Location AZ Occupation Part Time Electrician (semi retired, old) - EE retired. Jun 16, 2017 #22 Carultch said: So what then is the purpose of an 8 ft ground rod, if you need all 96 inches of it to be below grade, yet you have to have a couple/few inches above grade to attach the wire? Click to expand... you dont have to pay for that extra 2ft of rod, and you bang it down just below grade, clamp it, bury it.
Carultch said: So what then is the purpose of an 8 ft ground rod, if you need all 96 inches of it to be below grade, yet you have to have a couple/few inches above grade to attach the wire? Click to expand... you dont have to pay for that extra 2ft of rod, and you bang it down just below grade, clamp it, bury it.