Must be listed by a NRTL. Don't see any such labeling on container
I don't know when they changed to current design, been at least 40 maybe 50 years ago, but some of the oldest QO breakers out there don't have today's design for the load terminal on 15-30 amp breakers, and likely are only listed for one conductor.Like electricians there are good and bad HI's. Over the years I've dealt with some really bad ones especially when I sold my own house. They're taught to look for "double taps" often without a general understanding of why they're permitted or prohibited. I just write up something to explain their errors and move on.
True, they are a set of eyes to look at things in the home that might need attention and might be of interest to buyer and/or seller. What either does with the information report from said inspection is nothing more then information that can be used for purchase agreement reasons. None of the deficiencies is required by either party to be "fixed" it is just something they can use as a tool to get an idea of the condition of the home they are buying/selling. Nothing wrong with asking another professional their opinion on something in that report either.In many places Hi's are forbidden from citing code as they should be, after all they're not code inspectors.
QO has same terminals on 15-30 amp breakers. Homeline has same thing, so does NF (277/480 rated) up to 30 amps.The problem I've seen is that they WILL cite the correct code section (110.14), but they don't understand that if the device is LISTED for two wires per terminal, it meets that code. Other than Square D QO 15-20A breakers, I don't think there are any others that allow two wires per terminal, hence the problem.
I don't know when they changed to current design, been at least 40 maybe 50 years ago, but some of the oldest QO breakers out there don't have today's design for the load terminal on 15-30 amp breakers, and likely are only listed for one conductor.
In many places Hi's are forbidden from citing code as they should be, after all they're not code inspectors.
The problem I've seen is that they WILL cite the correct code section (110.14), but they don't understand that if the device is LISTED for two wires per terminal, it meets that code. Other than Square D QO 15-20A breakers, I don't think there are any others that allow two wires per terminal, hence the problem.
in this instance, there were no codes cited, just a recommendation to have an electrician investigate the "double tapped" breakers.
Those of you that offered advise, I thank you.
I had already gone to the Schneider website, printed and highlighted the spec sheets.
I went to the site today and made sure the load on the cited breakers was acceptable with every electrical item operating, wrote a letter, attached the highlighted spec sheet and collected payment.
Hopefully the customers sale will go through.
I'll be happy to give the owner a written statement that this is in compliance with codes and listing of the equipment involved, and an invoice of $200 for 10-15 minutes of work done at my convenience. $500 if you want it "immediately".They were just covering themselves as they are not qualified to make a determination of how safe the double taps are.
in this instance, there were no codes cited, just a recommendation to have an electrician investigate the "double tapped" breakers.
That is the proper course of action. There shouldn't be any code citation from an HI just a recommendation for further evaluation by a professional. Many times I have been called to investigate the findings on an HI report and like others here I explain why it's not a violation and cite to proper resource. If the HI is doing his job I leave the comments there.
I did have a HI report last year that was written by an idiot and I had no problem calling him out to the lawyers, realtor and buyer because he was IMO incompetent. The deal eventually fell through likely because of him.
I went to a home three weeks ago that listed double tap breakers, in the HI report, and ignored the 30 ground wires twisted together and landed in the lug on the neutral bar.
I'm not surprised and have seen similar things missed over the years. I would guess that it has to do with training they receive and the double tap is at the top of the list.![]()