Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
I have been rewiring several houses from knob and tube to modern Romex cable and code. However, with only 9 months part time as an apprentice I have been self teaching myself on NEC code in the process.
A couple things I would like to make less ambiguous:
NEC requires two separate 20 ampere small branch circuits in the kitchen, meaning two 12-2 Romex NM cables each being connected to a 20 ampere breaker or....
The code book can be ambiguous on this because 2 or more branch circuits can be interpreted as one NM cable connected to one 20 ampere breaker terminating it’s other end to an AFCI Tamper resistant receptacle and paralleling or BRANCHING to several more receptacles or 2 or more branch circuits. I absolutely hate the ambiguity of NEC wording, I assume NEC meant the first.
(Temperature correction factor already considered in wire and AFCIs and GFCI requirements also already factored in)
Also would like to get more info on mast height requirements, where to cut top, how to connect neutral
Also supply bonding vs loads size bonding one being based on NEC chart to the largest size conductor.
Also will I also have to use bonding bushings for all EMT entering breaker panel?
Can I get away with standard breakers with Temper resistant AFCIs On first Receptacle outlets (within 50ft of 12-2 and 70 ft of 14-2).
Neutral sizing and 83% reduction on feeders?
I do not know dryer or range or NEMA receptacle type to be used but will standard orange 10-2 NM romex Cable suffice For most applications?
House 1250 sq ft, 125 main breaker on standard split phase 120/240 utility
Thanks
A couple things I would like to make less ambiguous:
NEC requires two separate 20 ampere small branch circuits in the kitchen, meaning two 12-2 Romex NM cables each being connected to a 20 ampere breaker or....
The code book can be ambiguous on this because 2 or more branch circuits can be interpreted as one NM cable connected to one 20 ampere breaker terminating it’s other end to an AFCI Tamper resistant receptacle and paralleling or BRANCHING to several more receptacles or 2 or more branch circuits. I absolutely hate the ambiguity of NEC wording, I assume NEC meant the first.
(Temperature correction factor already considered in wire and AFCIs and GFCI requirements also already factored in)
Also would like to get more info on mast height requirements, where to cut top, how to connect neutral
Also supply bonding vs loads size bonding one being based on NEC chart to the largest size conductor.
Also will I also have to use bonding bushings for all EMT entering breaker panel?
Can I get away with standard breakers with Temper resistant AFCIs On first Receptacle outlets (within 50ft of 12-2 and 70 ft of 14-2).
Neutral sizing and 83% reduction on feeders?
I do not know dryer or range or NEMA receptacle type to be used but will standard orange 10-2 NM romex Cable suffice For most applications?
House 1250 sq ft, 125 main breaker on standard split phase 120/240 utility
Thanks