Home rewire from knob and tube

Status
Not open for further replies.
Electofelon I keep hearing the field is in favor of workers now, but when I looked in the past couple years I couldn’t find crap
 
So I am correct by feeding two 12-2 nm cables each to its own 20 ampere breaker, followed by first receptacle being ACI and those protected downstream liadside connection of AFCI? Thanks
No, not with NM cable. The breaker and AFCI receptacle would need to be listed together as a set.
 