We had a customer contact us for a quote to install a 20 kw Kohler generator, (that the customer has already purchased). The customer is adamant about placing the generator under a deck. Kohler literature says 60” from combustibles must be maintained. First, I do not believe 60” clearance could be obtained under this deck. Secondly, we are totally opposed to locating the generator under a structure of any type. For clarification, this deck is elevated on post and is open on three sides. Another contractor quoted the job stating that 36” clearance is adequate. I cry foul. We are not a
Kohler dealer, but the literature on line that we found says 60”.
My questions to you are: does the NEC or the IBC say anything about clearance other than complying with UL? NFPA 37 requires 60”. Generac clearly states that you shall NOT place their generators under a deck. All help will be appreciated. Even if we don’t do this job, I am trying to be sure the customer makes an informed decision. Thank you all.
Kohler dealer, but the literature on line that we found says 60”.
My questions to you are: does the NEC or the IBC say anything about clearance other than complying with UL? NFPA 37 requires 60”. Generac clearly states that you shall NOT place their generators under a deck. All help will be appreciated. Even if we don’t do this job, I am trying to be sure the customer makes an informed decision. Thank you all.