Sq. D Homeline makes a panel where the afci and gfci connect to the neutral bar. Does anyone know if a standard afci/gfci breaker (with the pigtail) can fit in this panel and is it compliant? @jim dungar
 
Sq. D Homeline makes a panel where the afci and gfci connect to the neutral bar. Does anyone know if a standard afci/gfci breaker (with the pigtail) can fit in this panel and is it compliant? @jim dungar
Yes to both questions, and you're not required to use the neutral terminal on plug-on-neutral standard breakers.
 
Yes to both questions, and you're not required to use the neutral terminal on plug-on-neutral standard breakers.
I agree that both plug on neutral and pigtail neutral breakers can be used.
I'm confused about your comment in bold. There is no plug on neutral standard breaker.
 
Sq. D Homeline makes a panel where the afci and gfci connect to the neutral bar. Does anyone know if a standard afci/gfci breaker (with the pigtail) can fit in this panel and is it compliant? @jim dungar
There is also a neutral bar/bus with screw slots along with the plug-on portion. So you can use the breakers w/pigtail, just connect the pigtail like normal on the older panels.
 
It sucks now when I get in a hurry and run into Lowe’s or the depot and grab my Afci or gfci breakers. When I get to the job it’s the new plug on neural breakers instead of the pigtail.🤬🤬🤬🤬🤯🤯
 