homemade manual transfer switch

Status
Not open for further replies.

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
The OP says " I'm thinking about doing a manual transfer switch". What he is proposing is not a transfer switch in any form. It is nothing more than a receptacle connected to the electrical system. No different than the practice of back feeding the dryer receptacle trick. As all have said, not compliant or safe. He does not seem to understand what a transfer switch does.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Note that when you hit reply, you can start typing after the [ /QUOTE ] section to add your comment. Hitting just reply and not typing more is just wasting a reply.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Your installation MUST be made so it is physically impossible to accidentally interconnect the two sources.

You may NEVER, EVER rely on "I'll remember, and nobody else will use the equipment."
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I agree with the others, use a listed transfer device and be done with it. With that said I am closing this thread.

Roger
 