http://i22.photobucket.com/albums/b334/steelbuster/P1010561.jpg
Almost Red Tagged today for this SE panel...
Almost Red Tagged today for this SE panel...
What do you mean "almost"? What did the inspector say? Are you asking us to "spot the violation," based on looking at the photo of the panel?Originally posted by steelbuster:Almost Red Tagged today for this SE panel.
300.7 Raceways Exposed to Different Temperatures.
(A) Sealing. Where portions of a cable raceway or sleeve are known to be subjected to different temperatures and where condensation is known to be a problem, as in cold storage areas of buildings or where passing from the interior to the exterior of a building, the raceway or sleeve shall be filled with an approved material to prevent the circulation of warm air to a colder section of the raceway or sleeve. An explosionproof seal shall not be required for this purpose.
I second that!Originally posted by allenwayne:
I think you did a fine bang up jobNeater than what I have seen some so called professional electricians do.
You came to the right place. Some of these guys will find fault with ANY installation.Originally posted by steelbuster:
Yes, I was asking for an opinion on the possible infractions in the panel.
Thanks and that sounds good.Originally posted by steelbuster:
The bare ground is going out to the supplementary ground rod. It exits through a drain hole in the LB.