Homeruns entering panel from trough
You don't want to strip them. The conductors are not labeled so they cannot be run by themselves through the conduit. It looks like you are fine with 20 NMs and 2-1/2" conduit anyway. If you really want to, it's easy enough to just add another conduit to make things easier and for the future.
-Hal
You mean the insulation isn't labeled? I can easily label the circuit of that's what you're referring too. If you don't mind showing me the nex article you're referring too
Sent from my Pixel 7 using Tapatalk
Also make sure that your cables are arranged so that you do not nave more than 30 CCC's at any cross section. With 40 CCC's (20*2) derating would force you to come up with a different installation.
Cross section in the wireway is the area where all the conductors cross paths?
I like using wire-ways for many applications. For the installation pictured I would have run the NM cables directly from the ceiling into the loadcenter. To cover the cables (2) 2x4's and a piece for 1/2 plywood/OSB or drywall would be much quicker.
Or just make that some one else’s issue and inform owner how to make it look pretty and leave. I’ll frame if I have to but I want to move to next job
Yes, let's say you put your nipple to the far left or right of the panel. You would have 40 CCC's at the cross section where the cables enter the nipple triggering derating. If that happens you cannot use a single nipple.
USE cable in interior?
Romex NM cable
I believe @Greentagger is referring to the existing service entrance conductors being Underground Service Entrance (USE) conductors (or cable) 338.12(B), USE is often dual rated as RHH / RHW-2 so it can be direct buried outside of a building (230.6) then transition to a raceway when it enters a building as RHW-2.
It has to do with UL. The individual conductors in NM are not 'listed'.
The code article they are referring to is 310.10, many inspectors say that when you strip the insulation off the NM or MC cable is is no longer a 'cable' your not using the cable wiring method anymore its now just wire that your using in a raceway wiring method and you need a wire type listed in 310.10 for the application.
Another common practice is stripping the insulation off SER cable and using the individual wires to make up meter to panel thru a chase, like that URD cable you have was used for.
My interpretation of that is if it starts as a cable type wiring method, it may transition into a raceway with the sheath stripped off to the first termination. That way some of the cable sheath still exists with the required markings.
My interpretation is its only a violation if you say strip a scrap piece of cable and install it in a raceway as you would normal wire
Would they not technically be listed if you left enough jacket in gutter- to identify there type and usage- it’s in the same raceway system is it not? So would it not matter?
My interpretation is if you start off starts as a cable type wiring method (NM, MC SER), you may transition into a raceway with the sheath stripped off to the first termination, does not matter where you start or how. The ampacity for the stripped 'cable' is still based on 334.80, and also the normally dry location 334.10(A) so you cant strip it then say go underground in PVC.
The issue is, when you try to punch in a 2" conduit on the top with all the knockouts, it turns into a mess.all of the knockouts get knocked out unintentionally
I have just screwed a 4S blank cover to the top and punched through both.
This entire concept is dumb. Why not require the conductors in NM cable to be marked? Many MC cables already use conductors with surface markings.
My opinion is that each point on the circuit between enclosures has a well defined wiring method which should be determinable locally, just by looking at a cross section of installation. If that cross-section is conduit and individual conductors, no cable jacket, it's not a cable wiring method at that point.
Cheers, Wayne