You are a newly hired electrician at chemical processing facility. You have been asked for a preliminary assessment of a proposed installation. Given a 3-phase 500KVA 480/240 Delta-Delta Transformer, determine both the primary and secondary side protection. The transformer will feed a service panel 15 ft away, what size THWN conductors are required?
The service panel for the transformer problem feeds 3-3phase motor loads.
208V, 10 hp, S.F. 1.0, 250ft away from panel
208V, 15 hp, S.F. 1.10 300 ft away from panel
230V, 7 1/2 hp S.F. 1.10 150 ft away from panel
What are required starter sizes?, What are required overload heater sizes?, What are required feeder sizes (conductors)-limit VD to 3% and note VD is per phase. Size required feeder protection. Provide conduits sizes for all feeders (EMT).
Thanks in advance!