Greetings,
There is absolutely ZERO technical reasons why Type TC Cable can't be used within a structure without being in a raceway or on a cable tray system (other than just code alone). Type TC under UL 1277 is constructed no differently than Type SE-R under UL 854, except for the fiberglass binder tape found in SE-R. Binder material or fillers are not required in Type TC unless it is deemed needed to maintain roundness. This is left up to the manufacturers discretion of course.
Also important to note that to be used in the 2017 NEC new allowance for one and two families, the TC Cable has to contain both Power and Control conductors which is a poor excuse for saying the use has been "expanded". However, it was pushed by the generator manufacturers (beginning with a G) and was originally intended only to encompass the ability to install a TC Cable from the ATS to the Generator for the power and control in the same cable......but it has morphed into being used as a Mini-Split Cable. The advent of both power and control in such a cable is well........lets not argue that one until we get the NEC changes to say....
Anyway....TC Cable goes through the same crush and impact testing as Type MC (UL 1569) and usually has an sheathing twice as thick or more than traditional Type SE-R Cable. However, the notice that you can't use Type TC in a building like other nonmetallic cable systems is to me....a FARSE to the industry (if you happen to read my public input on the subject). Lucky for me the CMP also agreed that type TC Cable was like any other nonmetallic-sheathed cable type system so I expect the doors to open for its more expanded use in 2020.
Here is what the NEC CMP agreed on :
In One- and two-family dwelling units, Type TC-ER cable identified for pulling through structural members shall be permitted. Type TC-ER cable used as interior wiring shall be installed per the requirements of Part II of Article 334 and Part II of Article 340.
Exception: Where used to connect a generator and associated equipment having terminals rated 75°C (140°F) or higher, the cable shall not be limited in ampacity by 334.80 or 340.80.
Informational Note No. 1: TC-ER cable that is suitable for pulling through structural members is marked “JP.”
Informational Note No. 2: See 725.136 for limitations on Class 2 or 3 circuits contained within the same cable with conductors of electric light, power, or Class 1 circuits.
HOWEVER...here is what is should have said....and will be proposed in 2020
In One- and two-family dwelling units, Type TC-ER cable containing both power and control conductors that is identified for pulling through structural members shall be permitted. Type TC-ER cable used as interior wiring shall be installed per the requirements of Part II of Article 334.
Exception: Where used to connect a generator and associated equipment having terminals rated 75°C (140°F) or higher, the cable shall not be limited in ampacity by 334.80 or 340.80.
Informational Note No. 1: TC-ER cable that is suitable for pulling through structural members is marked “JP.”
Informational Note No. 2: See 725.136 for limitations on Class 2 or 3 circuits contained within the same cable with conductors of electric light, power, or Class 1 circuits.
Now that is just one public input....the other if accepted would revise 336.12(2) to not specifically reference raceways or cable trays.....while reworking 336.10 to allow it in any building where it meets the "JP" tests that are required.