Re: Hooking Generator to Residential Load Center
I KNEW this would happen! You guys don't let anything get past you!
Ed,
I can tell you what wiring scheme and what properly grounded is as soon as a generator is defined. 2 wire, 3 wire, single phase, three phase, fixed, portable, nuclear....whatever it is, will dictate most of your answers.
For the sake of keeping things simple- ground according to manufactures instructions will do.
I presumed that the generator would be portable rather than stationary, single phase 120/240V, under 5kW, in our example. For the sake of answering your question, we will continue in that presumption. MOST commercial manufactures of home use portable generators already have a center tap bonded to the case of the generator, there is a main disconnect to a receptacle that supplies output. A grounding point is also typically furnished and it is here that the generator will be "properly grounded" to a suitable ground reference. Since the loads in the dwelling can be served from two supplies simultaneously (those deemed critical and those not) and can also have interconnection between the two power systems -through touch, shielding of low voltage cables, etc.- there is a need to bond the two electrical systems together. Since we are already having to "properly ground" the generator, it is best to also reference the existing building ground when grounding the generator so the two systems remain at the same potential.
When the transfer switch is put between the service-normal or emergency- and sub panel, both the transfer switch and sub panel must have neutral/ground separation.
If the neutral were solid, the ground reference would be at both the service entrance and at the generator. In my suggestion, the way to avoid the ground loop problems, tricky grounding and bonding is to keep the "separate" in "separately". Disconnect from one system, connect to the next using the same ground reference for both.
Not a huge concern; I guess you could use the equipment grounding conductor at the transfer switch to ground your generator and NOT switch the neutral. In my world (healthcare) solid neutral transfer switches cause a lot of power quality problems. I like the separation of this neutral here and that neutral there to keep stray voltages away. But that is a personal preference.