If you use a Square D Home Line or QO Main Lug panel you can use a back feed main breaker in it with the hold down clip and place a second two pole breaker sized for the generator next to it. Then get the transfer device KIT (QO DTI) that prevents both breakers from being on at the same time. The panel must be rated for use as service equipment.
If you use a Square D Home Line or QO Main Lug panel you can use a back feed main breaker in it with the hold down clip and place a second two pole breaker sized for the generator next to it. Then get the transfer device KIT (QO DTI) that prevents both breakers from being on at the same time. The panel must be rated for use as service equipment.