rhamblin
Senior Member
- Location
- Kaukauna, Wisconsin
My wife's grandfather got a great deal on a used whole house generator, and figures I can hook up the electrical. I'm fully capable of doing it of course, but the only problem is, I've never hooked up a generator before. I have the manufacturers instructions, and can figure out where all the wires go. The unit is a 12kw 240V single phase natural gas generator.
Regarding where to install the ATS, I originally thought I would reroute the wires feeding the main breaker, to the ATS and then add wire from the load side to the Breaker Panel. But then, the ATS wouldn't be protected by any OPD, so what is typically done here? Mount a single breaker (200 A) in a separate enclosure and then feed the ATS and then the panel? I don't know if the meter base has any main breakers in it, I guess if it does, then I wouldn't need the other breaker. If I do need a separate OCPD ahead of the ATS, maybe a fusible disconnect will be cheaper than a breaker in a separate enclosure?
Regarding the grounding, and let me know if my thinking is off here. I am thinking the ATS does not transfer the neutral, therefore the generator is not a separately derived system, and therefore I can just size the grounding conductor off of the ungrounded conductors and I won't need to drive a ground rod. Just bond the grounding conductor from the generator to the panel in the basement.
Question regarding 445.18, I'm thinking the plumber is going to be putting in a ball valve for the gas line coming out to the generator. If I can convince him to install a lockable ball valve, I won't have to worry about a separate lockable disconnect, right? Or can you use the main 200 amp breaker in the panel as the separate lockable disconnect, assuming it is lockable?
Regarding where to install the ATS, I originally thought I would reroute the wires feeding the main breaker, to the ATS and then add wire from the load side to the Breaker Panel. But then, the ATS wouldn't be protected by any OPD, so what is typically done here? Mount a single breaker (200 A) in a separate enclosure and then feed the ATS and then the panel? I don't know if the meter base has any main breakers in it, I guess if it does, then I wouldn't need the other breaker. If I do need a separate OCPD ahead of the ATS, maybe a fusible disconnect will be cheaper than a breaker in a separate enclosure?
Regarding the grounding, and let me know if my thinking is off here. I am thinking the ATS does not transfer the neutral, therefore the generator is not a separately derived system, and therefore I can just size the grounding conductor off of the ungrounded conductors and I won't need to drive a ground rod. Just bond the grounding conductor from the generator to the panel in the basement.
Question regarding 445.18, I'm thinking the plumber is going to be putting in a ball valve for the gas line coming out to the generator. If I can convince him to install a lockable ball valve, I won't have to worry about a separate lockable disconnect, right? Or can you use the main 200 amp breaker in the panel as the separate lockable disconnect, assuming it is lockable?