G george t. everett Senior Member Location New York Apr 2, 2003 #1 Do harmonics caused by non-linear loads cause aproblem on all three phase services or only on wye services?
Do harmonics caused by non-linear loads cause aproblem on all three phase services or only on wye services?
B bennie Esteemed Member Apr 2, 2003 #2 Re: Hormonics 3-phase Harmonics are a problem on all AC electrical systems. The self generated current is more apparent on a wye neutral due to being in the same time domain as the load current.
Re: Hormonics 3-phase Harmonics are a problem on all AC electrical systems. The self generated current is more apparent on a wye neutral due to being in the same time domain as the load current.
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 2, 2003 #3 Re: Hormonics 3-phase George, wye configurations are the real sufferers. A center tapped delta would see the same scenario as a center tapped single phase (single winding) transformer. Roger [ April 02, 2003, 07:41 PM: Message edited by: roger ]
Re: Hormonics 3-phase George, wye configurations are the real sufferers. A center tapped delta would see the same scenario as a center tapped single phase (single winding) transformer. Roger [ April 02, 2003, 07:41 PM: Message edited by: roger ]