J Joncampos3 Member Location San Antonio, Texas Occupation Electrician May 7, 2020 #1 Can you mix hospital grade MC and regular MC in a jBox. Wondering if there’s a code reference? In this situation right now just seeing if it’s okay.
Can you mix hospital grade MC and regular MC in a jBox. Wondering if there’s a code reference? In this situation right now just seeing if it’s okay.
W wlaricci Member Location Maryland Occupation Healthcare Electrical Maintenance Tech May 7, 2020 #2 Why would you need to do this? As long as the required patient care areas are wired correctly, I don't think the NEC says that you couldn't jump out of the same box to hit something not required to be hcf cable. Sent from my Pixel 3a using Tapatalk
Why would you need to do this? As long as the required patient care areas are wired correctly, I don't think the NEC says that you couldn't jump out of the same box to hit something not required to be hcf cable. Sent from my Pixel 3a using Tapatalk
J Joncampos3 Member Location San Antonio, Texas Occupation Electrician May 7, 2020 #3 Running hospital grade in exam rooms and regular in the corridor areas.
W wlaricci Member Location Maryland Occupation Healthcare Electrical Maintenance Tech May 7, 2020 #4 Shouldn't be an issue. Sent from my Pixel 3a using Tapatalk