charlietuna
Senior Member
The temp. of a three pole breaker is only the beginning of identifying the problem. Where? On the breaker is the heat being generated ? The breaker may be perfectly good with one poor terminal connection? Or maybe two poor terminal connections? Might be a bad bus connection? What is the ambient temp that the breaker is operating at? What i see with these spot monitors is a whole lot of uneccessary breaker replacements. Infrared equipment in the hands of a QUALIFIED operator is good for our trade and our customers. Circuit breakers on A/C and Elevator loads operating close to their rated maximum load WILL BE HOT !! You can change them every time you go back to that panel -- and they will be hot! With good equipment, a qualified thermographer can look at a three pole breaker and see where the heat is being generated, and if the internal fingers of all three phases look uniform in heat generation the breaker is doing it's job!! I owe it to my customers to find their upcoming problems using infrared equipment, but even more important, i don't want them replacing normal operating electrical equipment.