I discovered that the 110 outlet in the wellhouse indicates a hot ground with a standard outlet tester. The wellhouse subpanel is supplied by a 3 conductor, 240 volt wire originating from a 200 amp breaker at the main power panel many yards away. Both the ground and neutral are screwed into the ground bus in the main panel.
In the wellhouse, when tested with an ameter, the voltage reads 120 and 240 respectively, when contacting the ground bus OR the subpanel itself, inside the panel INSTEAD of the neutral bus.
The outlet and switched light running from one 110 bar and the neutral bar in the subpanel also only function when the outlet's or light's neutral wire is in contact with the ground wire instead of the neutral. The ground bus is not attached to a braided ground wire into the soil. I'm thinking this is a potential fire hazard not to mention a serious shock or worse.
Causes:
Mice chewing on the wires below the wellhouse?
Poorly wired by previous owner.
Water seepage into supply wires?
Improperly grounded at main panel?
Solutions / recommendations?
Any advice is welcome and greatly appreciated.
Thanks in advance,
Linespike
In the wellhouse, when tested with an ameter, the voltage reads 120 and 240 respectively, when contacting the ground bus OR the subpanel itself, inside the panel INSTEAD of the neutral bus.
The outlet and switched light running from one 110 bar and the neutral bar in the subpanel also only function when the outlet's or light's neutral wire is in contact with the ground wire instead of the neutral. The ground bus is not attached to a braided ground wire into the soil. I'm thinking this is a potential fire hazard not to mention a serious shock or worse.
Causes:
Mice chewing on the wires below the wellhouse?
Poorly wired by previous owner.
Water seepage into supply wires?
Improperly grounded at main panel?
Solutions / recommendations?
Any advice is welcome and greatly appreciated.
Thanks in advance,
Linespike