Commercial facility (restaurant) has a 20A 2P feeding a sub panel in the wellhouse
It was tripping repeatedly, I guess when the pressure pump would come on. They told me the breaker felt funny. I said it’s rarely a faulty breaker.
Checked it out today. Breaker feels and functions normally.
Voltage is 244 at the main panel, 239 at the pressure pump motor while the motor is running.
Amp draw is a little high at between 8.2 and 8.7. Nameplate FLA is 8.1
I am unable to replicate the issue, and it apparently hasn’t tripped for the last several days.
The thing that I noticed is that the case of the pump motor, (not the impeller housing) is hot, like too hot to touch.
Ventilation is good, it’s an open shed.
Anyone have an idea what might cause it to overheat like that? And could it be something that could cause an intermittent over-current situation?
Theal overload on the motor has not tripped either, that I’m aware of.
It was tripping repeatedly, I guess when the pressure pump would come on. They told me the breaker felt funny. I said it’s rarely a faulty breaker.
Checked it out today. Breaker feels and functions normally.
Voltage is 244 at the main panel, 239 at the pressure pump motor while the motor is running.
Amp draw is a little high at between 8.2 and 8.7. Nameplate FLA is 8.1
I am unable to replicate the issue, and it apparently hasn’t tripped for the last several days.
The thing that I noticed is that the case of the pump motor, (not the impeller housing) is hot, like too hot to touch.
Ventilation is good, it’s an open shed.
Anyone have an idea what might cause it to overheat like that? And could it be something that could cause an intermittent over-current situation?
Theal overload on the motor has not tripped either, that I’m aware of.