Barbqranch
Senior Member
- Location
- Arcata, CA
- Occupation
- Plant maintenance electrician Semi-retired
I can't tell for sure from the picture, but it looks like the meter has a low impedance voltage setting.
Now that you mention it, you're correct. That's a Fluke 117 with has a built-in low-impedance measurement option. But the OP wasn't using that setting.I can't tell for sure from the picture, but it looks like the meter has a low impedance voltage setting.
It's one thing to meter the wires, its another to verify the wires are on the right terminal. FWIW, I would have stuck the meter leads in the receptacle because I would not feel like going to the trouble of removing the device unless that test failed first.Sorry Mivey but I think Bill is right and I was wrong.
Sorry Mivey but I think Bill is right and I was wrong.
It's one thing to meter the wires, its another to verify the wires are on the right terminal. FWIW, I would have stuck the meter leads in the receptacle because I would not feel like going to the trouble of removing the device unless that test failed first.
t
Never mind, I just looked at the pics and he has a test plug set up.
We have been talking about this for what, four days? And we have yet to pull the receptacle to look at the wiring and the connections.
Wow.
I would have done that before posting anything about it, as well as looking into other points on the circuit.
I have been reading all your comments and giving them serious thought, but:We have been talking about this for what, four days? And we have yet to pull the receptacle ...
I have been reading all your comments and giving them serious thought, but:
[1] I haven't been back to the site during those four days.
[2] I was reluctant to pull anything and expose any non-finger-safe hot terminals because I was the only person there -- nobody to call 911 for me if the need arises.
190703-1207 EDT
It is not necessary to pull the receptacle to determine the likely reason for the problem.
In some ways it is possibly better to not pull the receptacle first and disturb something that may relate to the problem.
.
...I can't think of any reason not to remove the receptacle...
Every other receptacle in the house behaved as expected, but using only the Sperry tester and not following up with a voltmeter.
Did we already determine it's the only receptacle exhibiting this issue? If it isn't, then the problem likely isn't in that box. Find where all the problems are first. Then determine where to start removing things.
190703-1504 EDT
growler:
The problem may or may not be at this receptacle.
Realistically, the problem could be in the wiring just beyond the outlet box and pulling the outlet could move the wires such that the problem appears to resolve itself. But we could "what if" this to death. If it were me, I would have shut off the branch circuit breaker and pulled the outlet to inspect the wiring before doing anything else. Ninety-nine percent of the time, the problem is in the box.If anything changes when the receptacle is pulled then the problem was at this receptacle.
....These devices are not intended for use as comprehensive diagnostic instruments....