I agree. Which is why I stated (as did you) that he needs to find where the old 2-wire NM meets up with the new 2+G NM. I'm guessing that whoever did the wiring for the addition made some kind of ground connection at that junction and it has either become a bad connection, or the source of the ground was poor to begin with.
Around here people will extend an un-grounded circuits with three conductor cable and never worry about a ground connection. It doesn't show up until someone plugs in a tester so no one notices.
I love chasing down missing grounds on home inspection reports.
Yes, when he finds where the new cable connects to the old it should become apparent what was done.
If he doesn't have a ground then he may have to GFCI protect those three pronged receptacles or run a new home run ( or at least an equipment ground wire).