finster1
- New Jersey
I installed a 50a gfci for a hot tub with 3 Cu #6'S two hots and neutral and 1cu #8 ground. In the interior of the building I used 3/4 emt and on the exterior I used one inch pvc with 4 #6 cu conductors from the GFCI panel I installed. The inspector tells me for a hot tub the ground wire should have been a #6 to the gfci also from the panel and that the bond wire should also be a #6 solid to the grid under the concrete of the tub. I did install a #6 to the grid but I bonded the motors with #8 solid cu wire. So we have from the main panel 3 #6thhn cu and 1 #8thhn cu to the GFCI, ALL RUN IN 3/4" EMT to the GFCI. Than to the hot tub I have 4 #6cu thhn in non metalic pvc conduit and the hot tub bond is #6 under and I used #8 to bond the motors to the metal frame of the tub...I dont see any problem at all and have installed many this way before but this inspector thinks otherwise..........What do you you guys my peers think??????????I could read the code book all day long and make all kinds of interpetations....