We did a job recently where we had a hot tub set into a deck. I, of course, had them run the equipotential bonding in the dirt beneath the deck and around the tub as required.
The deck has wooden posts with metal piping running horizontally between the posts. You can actually turn the pipes thru the holes that were drilled. The NEC requires all metal parts within 5' of the tub to be bonded. Okay, so what value does it have to bond these rails.
If, theoretically, the deck has the equipotential bonding then the deck would have the same potential as the voltage in the earth (if there is any). So why would these pipes need to be bonded? They are going thru holes in the posts and any connection there should be the same as the deck. I am afraid by bonding the pipes then you may have a different potential between the rails and the deck.
We did not bond it but the inspector is requiring it. He is using the NEC appropriately however, I think it is a mistake. What do you think?
Btw, it is not that big of a deal to bond it, I just think it may do more harm than good.
The deck has wooden posts with metal piping running horizontally between the posts. You can actually turn the pipes thru the holes that were drilled. The NEC requires all metal parts within 5' of the tub to be bonded. Okay, so what value does it have to bond these rails.
If, theoretically, the deck has the equipotential bonding then the deck would have the same potential as the voltage in the earth (if there is any). So why would these pipes need to be bonded? They are going thru holes in the posts and any connection there should be the same as the deck. I am afraid by bonding the pipes then you may have a different potential between the rails and the deck.
We did not bond it but the inspector is requiring it. He is using the NEC appropriately however, I think it is a mistake. What do you think?
Btw, it is not that big of a deal to bond it, I just think it may do more harm than good.