daiashi said:How to derate wire for 75c hot tub terminals?Thanks![]()
I am using a 50 amp gfi breaker.I don't know where the inspector is gettinginfinity said:If the terminals are rated for 75 degrees then you can use the #8 THHN protected at 50 amps. What size OCPD are you using?