Hot tub derating
Have always ran #8 thhn in 3/4 conduit.However now local inspectors
are requiring #6 because of the heat build up with #8. on 75c. Terminals.
If the terminals are rated for 75 degrees then you can use the #8 THHN protected at 50 amps. What size OCPD are you using?
I am using a 50 amp gfi breaker.I don't know where the inspector is getting
his info however he or she is creating an unnecessary expensive.Thank you.
If you are using a 50 amp breaker and all the terminals are rated at 75 degrees C then you can use #8 THHN copper conductors.
The inspectors might be tring to use 110.14(C)(1)(a)(2) to say that you must use the 60 degree C column to get you ampacity. Show them 110.14(C)(1)(a)(3) this allows you to use the 75 degree C ampacity column as long as the wire and all the terminations are listed and identified for use at 75 degrees C.