Back to my original question.If 50 feet away likely will need labeling to indicate what it is for in most situations like that.
5 feet away and obvious line running from it to the hot tub, no marking should be necessary.
I would not label with language that may be used elsewhere on the house.Back to my original question.
Would a sticker that says “Emergency Disconnect “ same as used on a residential disconnect suffice?
IMO no. It does not properly describe what it is serving. The proper term is maintenance disconnect.Would a sticker that says “Emergency Disconnect “ same as used on a residential disconnect suffice?
680.13 Maintenance Disconnecting Means.
One or more means to simultaneously disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be readily accessible and within sight from its equipment and shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool, spa, fountain, or hot tub unless separated from the open water by a permanently installed barrier that provides a 1.5 m (5 ft) reach path or greater. This horizontal distance shall be measured from the water's edge along the shortest path required to reach the disconnect.
Per NEC 2023Back to my original question.
An Emergency Shut Off button that removes power to the 'pumps' is not the same as a maintenance service switch that disconnects all power.Emergency Shut Off
Correct. The OP used the term the term, Emergency Disconnect.. I think was he was confusing service disconnect with emergency shut off.An Emergency Shut Off button that removes power to the 'pumps' is not the same as a maintenance service switch that disconnects all power.
Whether or not that is the correct terminology per NEC is meaningless to most end users. Emergency Disconnect label on this isn't totally unacceptable IMO. But again unless it is arranged that it is rather obvious what it is disconnects I think it needs further clarification to the labeling.Back to my original question.
I agree. His question is can the sole label Emergency Disconnect be used to describe the function of the maintenance disconnect mounted 50' away. IMO no.Whether or not that is the correct terminology per NEC is meaningless to most end users. Emergency Disconnect label on this isn't totally unacceptable IMO. But again unless it is arranged that it is rather obvious what it is disconnects I think it needs further clarification to the labeling.
IMO no.Back to my original question.
If the switch is 50' away how do you know what it's for without a label?The bottom line is that no label is required at all, and the disconnect must be less than 50’ away. Labeling does not change the distance requirement.
My statement was with regard to NEC compliance. I said it wasn’t required. I didn’t say it’s not a good idea!If the switch is 50' away how do you know what it's for without a label?
The prevalent opinion is that being 50' away a label as to what the is function of the disconnecting means is required.My statement was with regard to NEC compliance. I said it wasn’t required. I didn’t say it’s not a good idea!
Playing devil's advocate.....The prevalent opinion is that being 50' away a label as to what the is function of the disconnecting means is required.