I would not accept a label or sticker that is like 50-feet away and only says, "Emergency Disconnect"
110.22: "...the marking shall include the identification and location of the circuit source that supplies the disconnecting means unless located and arranged so the identification and location of the circuit source is evident."
At that far away, it's just simply not evident IMO. The inspector will say this. If there is an emergency (God forbid) and they need to shut that thing down quickly, the person will be injured or dead before they can figure out that the little box 50-feet away that says only EMERGENCY DISCONNECT was meant for the hot tub. You want to label things better, it's one of the most important requirements in the code. Just look at what they did with 408.4(A), for panelboard circuit directory. YET we still see characters writing LIGHTS and OUTLETS (even though an "outlet" can be a light, a receptacle, or a junction box) with no further definition of where. You want to give the building occupant a decent chance of figuring out what the circuit is for. Now I'm rambling...