Darren Stutzke
Member
- Location
- Spokane Washington
- Occupation
- electrician
680.41 What does the last sentence in this code section mean?
680.41EMERGENCY SWITCH FOR SPAS AND HOT TUBS. A clearly labeled emergency shut off or control switch for the purpose of stopping the motor that provides power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5 ft.) away, adjacent to, and within site of the spa or hot tub. This requirement shall not apply to one family dwellings.
Our company has always installed a disconnect for a hot tub, we are quoting a repair and the disconnect is not within site of the tub so we were reviewing and I have never read that sentence in the section.
680.41EMERGENCY SWITCH FOR SPAS AND HOT TUBS. A clearly labeled emergency shut off or control switch for the purpose of stopping the motor that provides power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5 ft.) away, adjacent to, and within site of the spa or hot tub. This requirement shall not apply to one family dwellings.
Our company has always installed a disconnect for a hot tub, we are quoting a repair and the disconnect is not within site of the tub so we were reviewing and I have never read that sentence in the section.