hot tub feeders

Status
Not open for further replies.
Re: hot tub feeders

I have read it. It seems that if there are no lights or lights under 15volts, or if it isnt a cord connected unit then GFCI protection isnt required. If there is something I'm missing please clue me in.
 
Re: hot tub feeders

Can't clue you in without more details.

Check out: 680.42(A)(2), 680.26(B), 680.44, 680.43(A)(1), 680.43(A)(2), 680.43(C), 680.43(B)(1).

Without more details, I cannot be more specific.

../Wayne C.

[ September 19, 2003, 11:12 PM: Message edited by: awwt ]
 
Re: hot tub feeders

artical 680 dosent specify that GFCI protection is required for non-cord connected hot tub/spa that has no lights, or has lights operating under 15 volts. Is it permisable to feed such a hot tub/spa with standard circut protection?
 
Re: hot tub feeders

Karen read Art. 680.40 thru 680.44 only, there you will find your answer, goodnight. :p
 
Re: hot tub feeders

Thankyou Wayne, I have been pouring over and over this in artical 680... and I am not satisfied that I have a clear answer to this question. I don't want to charge someone for this when it is not needed.
 
Re: hot tub feeders

Hello Karen
It is nice to see a women post here who is in the 'industry'.

When you are using Art 680, it can be confusing. Section 680.42 requires you to refer to parts I and II of the Article. So you will treat the outdoor Hottub as a permanent pool. 680.42(A)(2) permits installation of cord and plug units with the specifics mentioned.
The circuit per say is not required to be GFCI protected, the 'equipment' is required to be protected.

Pierre
 
Re: hot tub feeders

This is a packaged hot tub/not feild assymbled, not fed from a receptical, therefore I can find no reason to GFCI this motor circut. The packaged unit is already bonded through the feeders going back to the originating panel.

Thankyou Pierre for your responce.
 
Re: hot tub feeders

This is a packaged hot tub/not feild assymbled, not fed from a receptical, therefore I can find no reason to GFCI this motor circut. The packaged unit is already bonded through the feeders going back to the originating panel.


Karen:

Charging the customer for additional safety is not
"NO REASON". Are you willing to comprimise safety regardless of what the NEC states?

Remember the NEC is the minimum requirements, going the extra mile for safety should not always be considered as a money saving idea.

I would err on the side of safety,
 
Re: hot tub feeders

Karen
I am not sure what you are trying to prove or state in your post, but there is more to the installation than just Art 680. Did you read the installation instructions that came with the unit? I am pretty sure that the instructions will require GFCI protection [110.3(B)]. There are manufacturers that are producing special disconnects just for this and you can bet your last dollar they would not if it was not required.Brian John has also provided some pretty good advice.
I will tell you that I have the luxury of installing systems way beyond the minimum of the NEC and most of my customers are very pleased for the added safety, convienence, and 'ADDITIONAL VALUE' that I provide.

If you are looking to distinguish yourself and company, give them more and don't compromise.

Pierre
 
Re: hot tub feeders

I think that 680.44 clearly states that either the outlet supplying the hot tub must be GFCI protected or the hot tub must have integral GFCI protection. I agree with Pierre's statement to look at the installation instructions. I'm sure it will clearly state the this unit needs to be supplied by a GFCI protected circuit or that it contains the required GFCI protection internally.
 
Re: hot tub feeders

Thanks for your reply. I do agree with providing my customers with as much safety as possible. I needed to know the code on this point so I have made an issue of this installation. I could'nt find a code reference directly adderesing my question so I decided to put it out as a question on this forum. I am still concerned about the motor tripping the GFCI (class A) though. I have been working in industrial and commericial mostly of late and have to rely on my code book for direct information. Nuances to residential installations are not necessarly mentioned in the code book.
I haven't been able to read the manufactures info on this tub, of course that information may have made all the difference. Gratefully yours, Karen...
 
Status
Not open for further replies.