There is a WAC rule (Wa state code) on hot tubs dating back 20 + years, as when hot tubs became popular, there were many that were not listed. You might might look at that rule, 296-46B section 690
The WAC rule, 296-46B-680 posted above by Tom Baker, wants only tested / listed hot tub packages, or field evaluation for adding heaters & parts listed separately.
Evaluation should fail if heaters can burn without water, which can damage the heater, result in excess current leakage, or fire, if left unattended.