jetlag
Senior Member
- Location
- Eatonton, Georgia
I got a call to connect a hot tub . The rating on the tub is 40a @240v. The owner has ran his own wire but not connected either end yet. He used 6/3 wg nm , The outside part he put in pvc. I know the code now calls for 4--#6 conductors and not the #10 EGC but I dont have to much problem with that since wont be inspected, My question is he purchase a 60 a a/c pull out disconnent he wants install near the tub because he says the on off switch on the tub doesnt work well and he wants to be sure the tub is off. Im not comfortable with the pull out disc on there and telling him he needs a hot tub 50 a breaker disconnect. Am I correct or is it ok to use the a/c disconnect? Also what would be the proper distance to install it from the tub?