Hot tub. Location of the GFCI breaker in the circuit.

jklr

Member
Location
Miss
Occupation
Electrician
I have a Hot tub to hook up and my plan was to install the 40amp gfci breaker in the main panel and set a Square D Homeline disco QO200TRCP at the hot tub. My question is after reading the manufacturers user manual it calls for the L1,L2 and N coming into the spa electrical box be connected directly to the gfci. I know that either way the circuit is gfci protected, but can I do it the way I planned or do I need to follow the manual and install a 40amp breaker at the main and then install a 50amp gfci spa pack (readily available from parts house) at the hot tub.
 

Attachments

  • Screenshot_20250503_195950_Chrome.jpg
    Screenshot_20250503_195950_Chrome.jpg
    444.6 KB · Views: 10
I have a Hot tub to hook up and my plan was to install the 40amp gfci breaker in the main panel and set a Square D Homeline disco QO200TRCP at the hot tub. My question is after reading the manufacturers user manual it calls for the L1,L2 and N coming into the spa electrical box be connected directly to the gfci. I know that either way the circuit is gfci protected, but can I do it the way I planned or do I need to follow the manual and install a 40amp breaker at the main and then install a 50amp gfci spa pack (readily available from parts house) at the hot tub.
In terms of code either way is fine, in my opinion.
 
You could have possible nuisance tripping with the GFCI in the main panel due to the distance. Plus, you can buy a spa disconnect with a 50A GFCI breaker in it cheaper than you can buy just a GFCI breaker. Put the 40A regular breaker in the main panel and the spa disc w/GFCI breaker at the hot tub.
 