sparky59 said:Has anyone checked the neutral amps on a 50 amp hot tub circuit to see what the actual load is? I have seen several that had the neutral reduced to #8 conductor. I thought i might save a few bucks when i buy that new roll of white.
peter d said:I actually called a hot tub company once and asked about this because they had a spec that insisted that all conductors, including the EGC, be #6. They had no clue what I was asking and just parroted back the same "minimum #6" spec that was in the manual.
I ended up running a #10 neutral and ground.
Liability of what? Nothing ever happening?Jim W in Tampa said:Is it worth the liability ?
peter d said:I actually called a hot tub company once and asked about this because they had a spec that insisted that all conductors, including the EGC, be #6. They had no clue what I was asking and just parroted back the same "minimum #6" spec that was in the manual.
I ended up running a #10 neutral and ground.
peter d said:I actually called a hot tub company once and asked about this because they had a spec that insisted that all conductors, including the EGC, be #6. They had no clue what I was asking and just parroted back the same "minimum #6" spec that was in the manual.
I ended up running a #10 neutral and ground.
peter d said:I actually called a hot tub company once and asked about this because they had a spec that insisted that all conductors, including the EGC, be #6. They had no clue what I was asking and just parroted back the same "minimum #6" spec that was in the manual.
I ended up running a #10 neutral and ground.
stickboy1375 said:Liability of what? Nothing ever happening?
electricmanscott said:If something goes wrong you will be sued NOT MATTER HOW GOOD, legal, correct, whatever, your installation was.
Everybody will be sued, that's the way it is. People are greedy, "Victims" tend to be the greediest.
See Station Night Culb Fire or the loser that is suing the maker of a bseball bat becuse a child was injured by a ball hit by that bat. There was no warning that the bat was dangerous.
I say lock those people up for stupidity.
quogueelectric said:The reason they want to do this is on a lot of hottubs the heater is 240 and many of the pumps and motors are 120 on a gfi internal to the control panel so the figuring is why run a #6 for the neutral when the max imbalance of the 120 v load is 20 amps. This is the reason.
I'd rather buy #6 white than a lawyer's time. It's hard to refute the manufacturer's opinion.LawnGuyLandSparky said:Yes, it's simple unbalanced load theory. Who cares what the instructions say?
#6 is no better than #10 when the imbalance is a few amps. Even if taken to task IFO a lawyer or prosecutor, they have to prove your guilt, you don't prove your innocence. How are they going to prove your #10 caused an electrical failure, the instruction booklet isn't scientific evidence. It's manufacturer's opinion.
LarryFine said:I'd rather buy #6 white than a lawyer's time. It's hard to refute the manufacturer's opinion.
frenchelectrican said:Sorry to pick on your mind today.,, but i just want to make sure i can see your side of view on this one.
Merci,Marc