Is it allowable to run a 60 amp 4 wire feeder to a hot tub from a 4 wire sub panel instead of the main breaker panel?
Oakey said:Is it allowable to run a 60 amp 4 wire feeder to a hot tub from a 4 wire sub panel instead of the main breaker panel?
Dennis Alwon said:Sure why not.
Pierre C Belarge said:If you are installing a 4-wire feeder to a panel that will supply an outdoor hottub, you will need to follow 680.25. He is correct in stating that an insulated Equipment ground conductor is required.
If you are installing a 4-wire branch circuit to an outdoor hottub, you can use a Chapter 3 wiring method inside the building 680.42(C). Do not forget 680.42(A)(1).
Do not forget to read all of the first paragraph in 680.42.
Dennis Alwon said:Pierre are you saying if the sub panel is existing that the feeder must go to a main panel for an outdoor tub?
stickboy1375 said:Didn't we have that discussion already?![]()
Dennis Alwon said:See you are young and still remember things. In my old age I contracted CRS. It is a common disease of us old folks. :grin:
Actually I did remember.