I reviewed 680 this morning and I am looking for some conformation of my understanding.
1st, here is the project. A hot tub installed outdoors about 3' from an existing deck. The hot tub is all non-metallic except for the actual motor. It requires a 50-amp 240-volt circuit. I plan on installing a 4-ckt subpanel (more than 5' away) as a disconnect (using #6 copper). The reason for the panel is to add low voltage lighting in the yard.
I believe I can run the #8 solid copper bonding wire from the motor housing to the sub-panel and am not required to run it back to the main panel (service disconnect) providing the sub-panel has at least a #8 copper ground installed back to the main panel (I don't know yet if I'm using a cable assembly or conduit/conductors). Confirmation?
Thanks,
HWS
1st, here is the project. A hot tub installed outdoors about 3' from an existing deck. The hot tub is all non-metallic except for the actual motor. It requires a 50-amp 240-volt circuit. I plan on installing a 4-ckt subpanel (more than 5' away) as a disconnect (using #6 copper). The reason for the panel is to add low voltage lighting in the yard.
I believe I can run the #8 solid copper bonding wire from the motor housing to the sub-panel and am not required to run it back to the main panel (service disconnect) providing the sub-panel has at least a #8 copper ground installed back to the main panel (I don't know yet if I'm using a cable assembly or conduit/conductors). Confirmation?