Is it possible that in that section of the code when it says protected by the "outer sheath" they are refering to romex as well?
Oakey said:Thx for the replies all.
My god I just priced a roll of 6/3 romex at $357.00 at the warehouse..
Ouch!
tacomafc said:680.42 (C) Interior wiring to outdoor installations. This artical says that as long as it is recognized in chapter 3 of the code and that it contains a copper equipment grounding conductor that is INSULATED!!!! SO I think you must then run a conduit with a insulated conductor that is not smaller than a 12 awg. Oh yeah and green as well.
680.42(C) Interior Wiring to Outdoor Installations. In the interior of a one-family dwelling or in the interior of another building or structure associated with a one-family dwelling, any of the wiring methods recognized in Chapter 3 of this Code that contain a copper equipment grounding conductor that is insulated or enclosed within the outer sheath of the wiring method and not smaller than 12 AWG shall be permitted to be used for the connection to motor, heating, and control loads that are part of a self-contained spa or hot tub or a packaged spa or hot tub equipment assembly. Wiring to an underwater light shall comply with 680.23 or 680.33.
mgmelec said:i'm also in central jersey, and have never failed, for using romex to the line side of a gfci disco . every inspector has his claim to fame, i agree that you should check with him first, rather than doing the job twice. i've also found that most inspectors will gladly take calls from contractors with code questions. it's also a good idea to get to know the inspectors in the areas you are working .not only, can a quick call can save you time and money, but the embarassment of explaining a red sticker to your customer
tacomafc said:Could you please explain a little more on the whole underwater light thing. And when would you ever call a disco a sub-panel?
A section of a boat that would sink if it were missing.infinity said:What's the definition of a subpanel?