Jakewhis said:I have a Job this weekend to extent a branch circuit to a Hot tub. I know that I need a 50 GfCI breaker, Proper Wire size, A disconnect more that 5 feet away but within sight. Is there thing else that I should be thinking about.
Jakewhis said:Is there thing else that I should be thinking about.
Jakewhis said:A disconnect more that 5 feet away but within sight.
jwelectric said:why the disconnect within 5 feet? is this a comercial installation?
stickboy1375 said:I think you misread his post.
I have not seen the Job yet, but what I was told is that it is a residential home and the Tub is setting on a deck.Dennis Alwon said:There is a lot to think about. Where is the tub being installed? Do you need equipotential bonding. Pipe where necessary, etc, etc.
Tell us more of the install
benmin said:Sounds like your well prepared. Only thing I can add is, you'll need to run conduit under the deck if you're not using UF or SE cable and check to make sure the hot tub has all the metal componants bonded by #8 CU. 98% of manufacturers do the bonding but it's always good to check.
Dennis Alwon said:Ummm. Don't think so. Once you leave the house and get outside UF and se are not approved wiring methods.
Because the two are not rated for this installation.benmin said:Well I just might learn something. Pls explain why I can not run SE or UF under a deck.
benmin said:Well I just might learn something. Pls explain why I can not run SE or UF under a deck.
680.42 Outdoor Installations.
A spa or hot tub installed outdoors shall comply with the provisions of Parts I and II of this article, except as permitted in 680.42(A) and (B), that would otherwise apply to pools installed outdoors.
(A) Flexible Connections. Listed packaged spa or hot tub equipment assemblies or self-contained spas or hot tubs utilizing a factory-installed or assembled control panel or panelboard shall be permitted to use flexible connections as covered in 680.42(A)(1) and (A)(2).
(1) Flexible Conduit. Liquidtight flexible metal conduit or liquidtight flexible nonmetallic conduit shall be permitted in lengths of not more than 1.8 m (6 ft).
(2) Cord-and-Plug Connections. Cord-and-plug connections with a cord not longer than 4.6 m (15 ft) shall be permitted where protected by a ground-fault circuit interrupter.
680.25 Feeders.
These provisions shall apply to any feeder on the supply side of panelboards supplying branch circuits for pool equipment covered in Part II of this article and on the load side of the service equipment or the source of a separately derived system.
(A) Wiring Methods. Feeders shall be installed in rigid metal conduit, intermediate metal conduit, liquidtight flexible nonmetallic conduit, rigid polyvinyl chloride conduit, or reinforced thermosetting resin conduit. Electrical metallic tubing shall be permitted where installed on or within a building, and electrical nonmetallic tubing shall be permitted where installed within a building. Aluminum conduits shall not be permitted in the pool area where subject to corrosion.
Exception: An existing feeder between an existing remote panelboard and service equipment shall be permitted to run in flexible metal conduit or an approved cable assembly that includes an equipment grounding conductor within its outer sheath. The equipment grounding conductor shall comply with 250.24(A)(5).
Dennis Alwon said:Check this out and then read art. 680.25(A)
I don't think that applies here.jwelectric said:Also don't forget the equipotential bonding required by 680.26
Jakewhis said:I have not seen the Job yet, but what I was told is that it is a residential home and the Tub is setting on a deck.
Dennis Alwon said:I don't think that applies here.
jwelectric said:Why not? .